(16-07-2018, 09:49 AM)Craig Wrote: That was run as a spur from the house consumer unit .....
That doesn't quite make sense. Either it's a spur from an existing circuit or it's got its own circuit breaker in the consumer unit.
If the MCB/fuse at the CU is 20A or less then there's no need for a small consumer unit in the garage/shed. The discrmination will be non-existent between a 20A MCB in the main CU and anything to feed sockets in the shed. Just feed the sockets directly and use a 5A fused spur for the lighting.
The only reason under those circumstances to use a small CU in the shed is if there isn't an RCD in the main CU. Then the shed CU can house and RCD for everything down there plus a 6A MCB for the lighting.
Craig's point about insurance is technically correct but unlikely to be a problem. If you've done it right then there's not going to be an insurance claim due to an electrical fault. About the worst I've seen with decently wired shed circuits is where the terminals of an isolator switch weren't properly torqued up and the switch almost melted under a heavy load. Unfortuante, as it's not always easy to torque up the terminals correctly and then re-torque after the copper has yielded under load.