FIrstly I should mention that this is notifiable work under Part P of the building regs but that many of us turn a blind eye to that sort of thing
Ideally a feed to sockets outside the house should be fed from its own circuit in the consumder unit. A 20 amp radial is usually fine unless you have a heavy load in your shed etc. The circuit MUST be protected by an RCD. If the outdoor cable is armoured or in earthed metal conduit the RCD can be at either end. Otherwise it MUST be at the consumer unit, to protect against accidental "gardening" etc.
It is theoretically acceptable to take an outdoor feed off a spur from a ring circuit in the house. The spur will be fused at 13A so if your maximum load is less than that (about 3kW) then there's no problem. If the ring is protected by an RCD that's fine. Otherwise use an RCD spur which is readily available.
Cable size may matter if the shed is a long way from the house. In practice if the lights don't visibly dim when you turn on the heater then 2.5mm is fine for up to 20A.
There may be complicated issues to do with exporting the earth from the house but unless you have a lot of other earthed metal in the shed then don't worry. If you do have a metal framed shed or lots of other locally earthed metal then we'll need to have the complicated discussion.
At the shed end, the easiest approach is to feed the sockets directly and a 5A fused spur for the lighting.

Ideally a feed to sockets outside the house should be fed from its own circuit in the consumder unit. A 20 amp radial is usually fine unless you have a heavy load in your shed etc. The circuit MUST be protected by an RCD. If the outdoor cable is armoured or in earthed metal conduit the RCD can be at either end. Otherwise it MUST be at the consumer unit, to protect against accidental "gardening" etc.
It is theoretically acceptable to take an outdoor feed off a spur from a ring circuit in the house. The spur will be fused at 13A so if your maximum load is less than that (about 3kW) then there's no problem. If the ring is protected by an RCD that's fine. Otherwise use an RCD spur which is readily available.
Cable size may matter if the shed is a long way from the house. In practice if the lights don't visibly dim when you turn on the heater then 2.5mm is fine for up to 20A.
There may be complicated issues to do with exporting the earth from the house but unless you have a lot of other earthed metal in the shed then don't worry. If you do have a metal framed shed or lots of other locally earthed metal then we'll need to have the complicated discussion.
At the shed end, the easiest approach is to feed the sockets directly and a 5A fused spur for the lighting.