(13-06-2018, 07:00 AM)ppppenguin Wrote: Nick, from your description you're measuring harmonics on the load side. For the health of the incoming mains it's the harmonics on the line side that matter.
For a lot of older SMPS you might as well give them DC from a UPS. Don't know about later kit with power factor correction.
On the load side of the UPS boxes, yes - that happens to also be the "line" side for all downstream kit (basically the whole office). I have checked the utility supplies too - they are very clean.
These are full on-line boxes, i.e. they have two parts - one takes the utility feed and converts it to DC to charge 4 tonnes of batteries up to about 200V; the other part takes the DC from the batteries and converts it to AC for the downstream kit.
You are correct in that the first thing most SMPS boxes do is to convert the incoming AC mains to DC, so with decent PFC you should not be troubling the upstream units much at all.
If you don't have PFC you should change the PSU,