The power distribution guys take some inspired guesses sometimes in the name of expediancy,
A case in point many years past now.
We were involved in building a sauna into a very swish new property at a desirable Cheshire location.
Total connected single phase load 15 or 12.5 kW depending on sauna element arrangement.
We ran 25mm SWA from the garage incomer 30m through the garden, buried.
New sub board and switch at the meter position.
Board arrived and connected to meter, all proper, no cowboy own connections. 100 amp meter.
On switching the sauna on the mains practically disappeared!
The feed to the head was a bit of concentric.
Board man pronounced feed inadequate but was not surprised. He remembered that the site had been occupied by one old house, probably an 80 amp max feed. They had spliced the 4 new 100 amp feeds for 4 upmarket properties onto this existing old spiral wrapped cable.
I bet these houses have a good few kw of solar power going down that same old cable now.
A case in point many years past now.
We were involved in building a sauna into a very swish new property at a desirable Cheshire location.
Total connected single phase load 15 or 12.5 kW depending on sauna element arrangement.
We ran 25mm SWA from the garage incomer 30m through the garden, buried.
New sub board and switch at the meter position.
Board arrived and connected to meter, all proper, no cowboy own connections. 100 amp meter.
On switching the sauna on the mains practically disappeared!
The feed to the head was a bit of concentric.
Board man pronounced feed inadequate but was not surprised. He remembered that the site had been occupied by one old house, probably an 80 amp max feed. They had spliced the 4 new 100 amp feeds for 4 upmarket properties onto this existing old spiral wrapped cable.
I bet these houses have a good few kw of solar power going down that same old cable now.